Issue

After a Xenta download through the system Plugin the daylight savings mode is changed in the controller that was downloaded

Environment

Vista 5.x.x

System Plugin

Cause

The time setting in the System Plugin is applied to the Xenta controller at the time of download.

Resolution

In the system Plugin under the TAC network pane right mouse click on the TAC network and select Configure Time Settings.

 

From this window set the Time zone and daylight savings mode.

When finished select ok and then update the Vista database.