Decoding Software Revision Change entries in controller error log.

Issue

When the firmware in a Continuum second generation controller is changed via uprev flash file, the controller adds an informational item in its error log that includes the FROM and TO versions.

This article describes how to get those revisions from the error log.

Environment

bCX

CX9680

ACX5720/40

Cause

Documentation

Resolution

Following an uprev operation there will be three new Informational entries in the error log

Example:

6660 I 01/01/1989 00:00:00.00  0x00006409 0x09289b00 0x0190da1c 0x00008748 0x0000d384
                                        Software revision change
6661 I 01/01/1989 00:00:00.00  0x00006409 0x09289b00 0x0190da40 0x000025d0 0x00200b3f
                                        Software revision change
6662 I 01/01/1989 00:00:00.00  0x00006409 0x09289b00 0x0190da64 0x000025d0 0x00200b41
                                        Software revision change

The last column in the entries contains the version number information.

The first entry with a value of 0x0000d384 in the example above can be ignored

The second entry specifies the FROM version, in the example above the controller was flashed FROM 2100031 (0x00200b3f)

The third entry specifies the version the controller was flashed TO. in the example above the controller was flashed TO 2100033 (0x00200b41)