Default List views are missing columns after being re-created with Continuum database initialization update database option.

Issue

After a missing or deleted default list view is re-created using the Continuum database initialization utility; the list view does not contain any columns.

download (2).png

Environment

Cyberstation

Cause

This issue is caused by a Continuum defect issue that cannot be corrected at this time. QC#2222.

Resolution

There are several workarounds that can be used to resolve this issue.

1)      Columns can be manually added back to the list views re-created by the database update option.

2)      The default list views can be reimported from the DefaultListViews.dmp file in the Continuum folder.  This would overwrite all default list views there by losing any customization to existing list views.

3)      Individual list views can be imported from a dump file created from another Continuum Systems to provide pinpointed recovery of certain listviews.