Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Definition clarifications for Thermistor Type in Technical Reference Guide for StruxureWare Building Operation

Issue

Definition clarifications for Thermistor Type in Technical Reference Guide for StruxureWare Building Operation

Environment

StruxureWare Building Operation site with Thermistor temp sensors

Cause

In the image below of the technical reference guide for StruxureWare Building Operation on page 3164 the accuracy of the supported thermistors seems to be difficult to decipher or at least very hard to figure out what accuracy goes to what thermistor type.

The issue is the input specifications does not clearly separate the Thermistor type (Continuum, I/NET, etc) with the accuracy. If there was a line or something to separate the accuracy definitions from each other that would help. What defines one set of values from the next? The ending of the parenthesis defines the end of the information for each sensor type, but this is not clear. 

Resolution

A defect has been recorded and it has been requested that in the next release of the Technical Reference Guide for StruxureWare Building Operation, this be corrected and offer clarification as to the accuracy with a Hard Return. The lines are actually separated by the end of the parenthesis, but this is difficult to decipher.
 

Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
‎2018-09-06 12:55 PM