Distribution Server MFC error, Application has stopped

Issue

CX Controller and children i2 devices moved from one DB to another via ASCII dump file.

Now when reloading the CX without the children i2 devices getting MFC error on reload of Controller when the IE table is being reloaded.

Environment

CyberStation

CX controller

I2 Infinet devices

Cause

Because all the controllers have been moved to a new DB the information in the  IE table in the I2 devices is invalid.

Resolution

Must reload the CX including its children i2 devices, this will ensure that a new IE table is sent to all devices as the devices will be reset and reloaded.