Does the bCX1-CR-INF (bCX9640) have any BACnet objects or functionality at all?

Issue

Need to use a controller that has no BACnet functionality due to network security limitations on site.

Environment

Continuum

bCX1-CR-INF (bCX9640)

Cause

A customer has a site with restrictive network security requirements and BACnet devices (or any other open protocol) are not allowed.

Resolution

The bCX9640 is an Infinet protocol controller only. This version of the bCX firmware does not have the BACnet stack installed, and there are no BACnet points able to be created in this controller. You will be fine to use this controller where BACnet support is not required or allowed.