Issue

Enterprise Network Server BTL Certification

Environment

I/A Series G3 3.6.35 BACnet Advanced Operator Workstation (B-AWS)
I/A Series G3 3.6.35 BACnet Operator Workstation (B-OWS)

Cause

The PIC statements for the I/A Series G3 Enterprise Network Server for BACnet Advanced Operator Workstation and BACnet Operator Workstation is available from Schneider Electric. However, they are not listed on the BTL website under Schneider Electric. 

Resolution

Schneider Electric is focused on maintaining BTL listings for servers and controllers that are an active part of the SmartStruxure solution. There are no plans to add or renew BTL listings for products that are only supported by TAC I/A Series systems at this time. Existing listings that don't apply to SmartStruxure solution will remain on the BTL website until they expire. Schneider Electric product BTL listing can be found here.