Erasing NOVRAM from ASCs

Issue

Erasing NOVRAM from ASCs

Environment

I/NET Seven Site

Cause

How to erase the firmware and programming in the ASC 

Resolution

There is a way for users to erase the firmware and programming in the ASC by following the following steps:

Note: take care that you do not clear the memory on a stand-alone ASC with no SLI or I/NET computer with which to perform step 6! This procedure does not just reset the parameters, it removes the entire application.

  1. Remove power from the ASC.
  2. Place DIP Switches 6-12 in the off (0) position.
  3. Apply power to the ASC, and then remove power again.
  4. Place DIP Switches 6-12 in the on (1) position.
  5. Apply power to the ASC.
  6. Download the UPD file by selecting Update ASC to restore it to defaults.

On occasion, it may be necessary to repeat steps 1-5 twice.