Error Code 80044E34 during Equalization

Issue

Utilizing Equalization and an error code comes up that the file master is unable to add article, code 80044E34

Environment

I/NET Seven

Cause

The file InetEqzCr.dll needs to be manually registered.

Resolution

From the windows “Command Prompt” (CMD).

  1. Change the directory to the following path; C:\ProgramFiles\ Inet Seven\
  2. C:\ProgramFiles\ Inet Seven\ regsvr32 ineteqzcr.dll
  3. Close or exit the prompt.
  4. Restart I/NET
  5. Demote all of the clients and the file master
  6. Re-promote them again.
  7. Equalization should be working properly now.