Error: LNS #6 lcaErrObjectNotFound error #6 NLCredits Generator "The object was not found"

Issue

When launching NLCredits Generator, you get the following error : THE OBJECT WAS NOT FOUND. (SUBSYSTEM: LNS, #6) 

An object has been requested by name or index that could not be found in the databases.  Typically, this would be a request from a LNS collection object with a bad name or index.

Environment

NL220
Vista
LNS

Cause

An object has been requested by name or index that could not be found in the databases.  Typically, this would be a request from a LNS collection object with a bad name or index.

It should be noted that this error can also occur in some implicit assignments. For example, if the network interface to be used has not been explicitly assigned to the appropriate property, LNS will continue using the network interface previously assigned to the ActiveRemoteNI or NetworkInterface property, respectively.

In such a scenario, this exception could occur even though no explicit assignment has been made, indicating that an implicit assignment maps to an unavailable object.

A monitor set may be created while offnet (System.MgmtMode is set to lcaOffNet); however, a monitor set cannot be opened while offnet. Furthermore, attempts to query the MonitorSet.IsOpen property will get the error "The object is not found (Subsystem: LNS, #6)" when offnet

Resolution

  1. Launch NL220 and check if there is a project with a name only composed by alphanumerical characters (for instance, something like 82807E44116C482).
  2. Delete the project if you find it.
  3. Go to C:\NLPrj and manually delete the directory of the project you've deleted in NL220.