Error: NS #138 lcaErrNsNetworkInterfaceState

Issue

Local network interface is in the wrong state (e.g. unconfigured). 

Environment

LonMaker
NL220
Vista
LNS

Cause

Local network interface is in the wrong state (e.g. unconfigured).

Resolution

When you encounter this error, set the network management mode to lcaMgmtModePropagateConfigUpdates (0) by writing to the MgmtMode property of the System object. Then, re-commission the network interface, if necessary

Run the LNS Database Recovery Wizard: If you are recovering through a PCC-10, PCLTA-10 or PCLTA-20, use the LonWorks Plug 'n Play Control Panel to select the NSI NI Application. Otherwise, error "NS #138 (Local interface is in the wrong state (unconfigured)" is reported, then "NS #67 system is not open)", then "LNS #55". Finally, the LNS Database Recovery Wizard only gives you the option to cancel the recovery.

see also Echelon support article 190