Error: NS #50 lcaErrNsDblimit "An unspecified database limit was exceeded. (Subsystem: NS, #50)"

Issue

An unspecified database limit was exceeded.

Environment

LonMaker
NL220
Vista
LNS

Cause

You will get this LNS error when the maximum number of devices within a network (32385) is exceeded.

Resolution

Run the LNS Database Recovery Wizard: If you are recovering through a PCC-10, PCLTA-10 or PCLTA-20, use the LonWorks Plug 'n Play Control Panel to select the NSI NI Application. Otherwise, error "NS #138 (Local interface is in the wrong state (unconfigured)" is reported, then "NS #67 system is not open)", then "LNS #55". Finally, the LNS Database Recovery Wizard only gives you the option to cancel the recovery.