Issue

Error code 2041 when reading a SNVT from a TAC Xenta 103

Environment

TAC Xenta 103

Cause

Bindings may have been made with LonMaker after the device was created in TAC Vista. The wrong address is referenced in TAC Vista.

Resolution

Error code 2041 means no answer from the TAC Xenta unit.

  1. Invalidate the addresses in TAC Vista
  2. Reread the addresses for the unit using status window for the unit.