Error during BACnet b3 download

Issue

Error during BACnet b3 download

Environment

Automation Server WorkStation

Cause

Binding sending data to a point during the download process

Resolution

During download to a b3 controller you may see the error - Unknown object

Module: BACnet plugin
Module code : 0
Technical info: BatchedWritePropertyError

This error is benign and can be ignored, it happens when a binding sends data to a point during the download process

 

Also check out the SmartStruxure - b3 Engineering Process - Part 6 Downloading Quick-Help video on the Exchange.

NOTE
The "BatchedWritePropertyError" may also be seen with "Property value out of range" rather than "Unknown Object", in this case check the properties/settings of the BACnet Object, the channel may be out of range or an Expansion Module may be required