Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Error when trying to copy/paste objects from on MP-X device to another

Issue

Copying objects from one MP-X device to another results in a validation error. "Property value '<object type>' already assigned"

 

 

Error Screenshot.JPG

Product Line

  • MPx series
  • EcoStruxure Building Operation

Environment

  • Building Operation Workstation
  • Building Operation Multi-purpose Controller
  • Building Operation Multi-purpose VAV

Cause

The Object ID is already used within the destination device

Resolution

This functions as design. To resolve this:

 

  1. Manually enter the Object ID when creating files that may be copied to other MP-X devices. One may choose to use blocks of IDs up to 64,999.Manul ID SC.png

     

    2. Utilize the import/export function within EBO which will import the BACnet objects using the next available Instance IDs.