Issue

Extended Logs not showing up in the Reports Server

Database table tbLoggedEntities does not contain trend data.

Environment

Report Server

Cause

Extended Trend logs must reside on the ES and must have the "Include in Reports" parameter set to "True"

Resolution

  • Ensure the Extended Trend Log resides in the ES. If it is in an AS, you can create another Extended Trend Log in the ES with that as the reference.
  • Ensure that all Extended Trend Logs that you wish to see in Reports have the parameter "Include in Reports" set to "True"