FieldServer Bridge in Lon network with more then 15 devices

Issue

FieldServer Bridge in Lon network with more then 15 devices

Environment

I/NET or Vista Site

Cause

Can a FieldServer bridge communicate with more then 15 Xenta controllers?

Resolution

A FieldServer bridge can communicate with more then 15 Xenta controllers despite the address table limitation found with implicit addressing. This requires that the bridge be programmed for explicit addressing which requires the knowledge of the controllers node number and SNVT index numbers. This is useful for situations where you are interfacing to a non LonWorks device that needs to communicate values to more then 15 Xenta or LonWorks controllers.