Forcing a value from the BACnet front-end will be overridden by the Lua script

Issue

When Forcing a vlaue from SBO, it is just overwritten by the Lua script all the time.

Environment

MPM

SE8000

Cause

By default, the MPM executes the program once every second, so if written simply like:

Output_1 = Off

the output will be turned Off every second.

Resolution


Declare a few variables in the Lua script that will help you implement the logic you need, here is an example:

--------------------------------------------------------------------------------------
var("Override_Status","ME.BV1")
var("Override_Value","ME.BV2")

if changed.Override_Status and Override_Status == 1 then
ME.BO1 = Override_Value

elseif changed.Override_Status and Override_Status == 0 then
ME.BO1 = ME.BI1
end

--------------------------------------------------------------------------------------

Basically, an override status points will act as a "Override button", and when it is active, The output will be equal to override value specified in SBO.

Else, if it is disabled, the output will be set to what ever you currently have in your script. In the example above, the output will be equal to the input.