Issue

Function Blocks as object controller

Environment

StruxureWare Building Operation FB Program at site

Cause

When commissioning the local node with a LNS tools (NL220), one cannot see the functional blocks as object controller in the LNS tool, but rather have all the SNVT in the static node. Is it normal? The problem is, if one has a lot of SNVT, it is not clear.

Resolution

Functional blocks created do not have a functional block index to be able to present them correctly. All Functional blocks have same index causing the presentation issue mentioned above.