Get Error message "Error: Unable to create blueprint file" when trying to download to Xenta device

Issue

Get Error message "Error: Unable to create blueprint file" when trying to download to Xenta device

Environment

  • TAC Vista
  • Xenta 301
  • Xenta 302
  • Xenta 281
  • Xenta 282
  • Xenta 283
  • Xenta 401

Cause

This can be caused if one or more of the I/O modules from the device does not have any subnet/node address defined.

Resolution

  1. Click on the Xenta in Workstation
  2. In the pane to the right double click on $IO
  3. Right click and select properties on the I/O modules
  4. Make sure that all modules have subnet node defined.
Tags (1)