Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Graphic pipes are missing from Px pages when viewed via a Web Browser.

Issue

Graphic pipes are missing from Px pages when viewed via a Web Browser, however pipes are displayed when viewed via WorkBench.

Environment

Niagara G3, ENC-520

Cause

The needed kitPxHvac module was missing from the ENC-520. It seems the kitPxHvac module was not installed to the ENC. Usually all required modules are automatically installed to the ENC at the time of a station install, but for some reason the kitPxHvac module was not installed.

Resolution

Manually install the kitPxHvac module to the ENC

- Open the Application Director window for the ENC hosting the graphics
- Double-click on Software Manager
- Select the kitPxHvac module from list and click the “Install” button at the bottom of the screen.
- Click the “Commit” button to install the kitPxHvac module to the ENC
A reboot of the ENC should not be required.

Open a new Windows Browser and browse to the ENC. The pipes should now display correctly in the graphics.

Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
2 weeks ago
Updated by: