High and Low Setpoint Limits on MN-HPFC Controller do not appear to be operating properly.

Issue

High and Low Setpoint Limits on MN-HPFC Controller do not appear to be operating properly.  The local high setpoint limit appears to limit only the high heating setpoint and the local low setpoint limit appears to limit only the low cooling setpoint.  What do I have configured wrong?

Environment

MN-HPFC with local setpoint control

Cause

As designed.

Resolution

As noted in the MicroNet Heat Pump / Fan Coil Controller reference manual, F-26174. the "Local Hi Lmt Spt" defines the Maximum value for the local heating setpoint and the "Local Lo Lmt Spt" defines the Minimum value for the local cooling setpoint for use when the heating/cooling setpoint is set through the MN-SDK deluxe sensor.  This operation is also documented in Technical Bulletin 01-01.