How can a setpoint programmed using a nci-type snvt, in a MNL controller, be controlled and displayed in a Niagara R2 station?

Issue

How can a setpoint programmed using a nci-type snvt, in a MNL controller, be controlled and displayed in a Niagara R2 station?

Environment

MNL controllers

Niagara R2

Cause

Site programming was done years ago and the end customer wants to now add the ability to change a setpoint in all the MNL controllers from a Niagara R2 graphic.  The setpoints were configured using a nci-type snvt (ex: nciSatConfig1).

Resolution

A nci-type snvt can be displayed and commanded from a Niagara R2 station. One method to provide both:

  1. In the DynamicCmd object > Config tab, set it up like this:
  2. Visual tab, set it up like this:
  3. In the UnitConversion > Config tab, set it up like this: