Issue

How can it be determined what LonWorks Program IDs are supported by the Niagara G3 system?

Environment

G3 WorkBench (all builds)

Cause

N/A

Resolution

  1. Create and install a test station on the localhost.
  2. Open the test station in WorkBench then add LonNetwork to Drivers from the lonworks Palette.  
  3. Double-click on the LonNetwork.
  4. Double-click on the Local Lon Device listed under Database and set the following properties
    • Channel ID: 1
    • Subnet: 1
    • Node: 127 and click OK to accept changes.
  5. Right-click on LonNetwork and open the Lon Utilities Manager.
  6. Select the Local Lon Device then choose the Command of Reports and Sub-command of program Ids.
  7. Execute the command and a listing of all programIDs for the shadow objects found in the local My Module  library will appear.
  8. To save - highlight all program Ids and use “Ctrl C” to save to file.