How does the controller-resident schedule work in a Revision 11.x MicroSmart controller?

Issue

How does the controller-resident schedule work in a Revision 11.x MicroSmart controller?

Environment

MicroSmart controllers revision 11.x and 10.x

Cause

Main DMS panel and/or NC panel were removed.

Resolution

With the loss of schedule control from the DMS or NC, each controller has two built-in schedules numbered 1 and 2.

The Start/Stop point requiring a schedule can be assigned either one of these schedules followed by a letter A or letter B.

Letter A stands for 'always' and letter B for 'backup'.

With no DMS or NC present, enter the schedule as 1/A or 2/A.  Assign 'off' and 'on' times as required.
Remove any reference to a DMS or NC schedule number (i.e. set it to a value of 00). 