How many Import Export points can each controller hold?

Issue

Is there an IE table size limit?

Environment

Import Export Limits

Cause

Using IE is the most efficient way to pass data around a Continuum system, when the tables are full the system will revert to a Point to Point method.

Resolution

The limits are 255 in the Infinet controllers and 65535 in the CX level controller.

In the CX level controllers this is for communication to the Infinet network and any pier to pier communication between CX's.

Also see the object limit for the Infinet i1 and i2 controllers, that can be found in Lessons Learned Article #5417.