How to Add Separate Bit of Modbus Register to Device Template

Issue

Some Modbus registers contain many separate bits to stand for different meanings. Sometimes only several of them are needed to be added to device template in Vista.

Environment

Vista

Modbus

Cause

This kind of application is required for some projects. 

Resolution

  1. Create a new device template.
  2. Fill the name, full address and other information of the register.
  3. In the Bit Mask column, fill the Start and Stop bit of the register. For example, if only the 2nd to the 5th bits are needed, then fill “1” in the Start bit while “4” in the Stop bit. Then only the bits needed are added into the device template.