How to Mass Create Trend Logs and Extended Trend Logs

Issue

How to Mass Create Trend Logs and Extended Trend Logs

Environment

Workstation

Cause

If you do not create Trend Logs at the same time you create the points or values, it is possible to create several trend logs or extended trend logs as the same time.

Resolution

For this example, we assume all of the values are in the same folder. You can hold down SHIFT to select multiple adjacent objects, or CTRL+click to select non-adjacent values

Mass Creation of Interval Trend Logs

  1. Select all of the Values you wish to add the same type of Log to
  2. Right Click and select New>Trend
  3. Select the Log type and the settings you wish to use.  Note that the log name will be the values name with either a prefix or suffix defined by the user
  4. Be sure to Select a useful folder location
  5. Click Next
  6. Set the Interval Settings
  7. Click Next
  8. Click Create

Mass Creation of Extended Trend Logs

  1. Select the group of Logs you wish to create Extended Trend Logs for
  2. Right Click and select New>Extended Trend Log
  3. Enter the desired settings. Just as above, the Extended log will use the Log' name plus either a prefix or suffix
  4. Be sure to Enter an appropriate Location.  Use a folder on the ES if you wish these logs to show up on the Reports Server
  5. Click Next
  6. Configure the Extended Log as desired
  7. If you want all of these logs to show up in the Reports Server, set the "Include in reports" property to "True"
  8. Click Create
Tags (2)