Issue

Access control site where doors are typically held opened during business hours don't want annoying alarms during the day, specifically the site wants door ajar alarms sent only from 5:00 PM (17:00) to 8:00 AM (08:00)

Environment

CyberStation

Cause

Configure a separate Event Notification with recipient time range specified in 'From Time' to 'To Time' columns.

Resolution

When configured as above the alarms associated with the notification object will be logged in the database but not displayed in the Alarm Viewer during business hours.