Issue

Unable to change set point from the thermostat when adjusting the value from a BAS

Environment

Smart Struxure Lite

Cause

Misconfiguration of the object and BACnet priority level

Resolution

1)     When discovering the object from the BMS, it will integrate as; type: numeric point | Property ID: Present value | Name: Occupied cool Setpoint as an example. The variable will be for reading only the actual value set.

 

2)     To change values from the BMS and thermostat, the object shall be configured as follow:

·        Type: numeric WRITEABLE

·        Enabled: True

·        Property ID: RELINQUISH DEFAULT

 

From the thermostat, If the value is highlighted in RED by going to set point page 1/2, the object is misconfigured repeat step 2