How to create i2xxx and b3xxx controllers from a CSV dump file.

Issue

How to create i2xxx and b3xxx controllers from a CSV dump file.

Environment

Continuum

i2xxx Controllers

b3xxx Controllers

Cause

In this scenario they wanted to create the beginning of a site database from CSV dump files before deploying on site. 

Resolution

It seems that when creating an i2 or b3 object, the path is also required when defining the comm port. Make sure to add the path to the Port field and this should allow the controller object to be created. See the original CSV I exported below, how it was modified, and then imported back in successfully.

Original Export to CSV

InfinityInfinetCtlr
Name,InfinetId,Port,DeviceId,SerialNum,Alias,CntrlType
i2_850,32,Comm1,Network1\ACX11_10th,11111,i2_850,i2920

Modified Import CSV

InfinityInfinetCtlr
Name,InfinetId,Port,DeviceId,SerialNum,Alias,CntrlType
i2_920,32,Network1\ACX11_10th\Comm1,Network1\ACX11_10th,11111,i2_920,i2920

Now, this import does complain about the CntrlType in the distribution Properties window but does create the controller and sets the type correctly. If you don't want any errors you can remove the CntrType attribute and the controller object will still be created but will default to a 240 controller. See below.


Import CSV without CntrlType

InfinityInfinetCtlr
Name,InfinetId,Port,DeviceId,SerialNum,Alias
i2_920,32,Network1\ACX11_10th\Comm1,Network1\ACX11_10th,11111,i2_920
 

This can then be changed to whatever controller you require through the controller Device object dialog.
 