Issue

User can’t disable the fan in heating mode

Environment

  SER7000 | SER8000

Cause

 Misconfiguration of the thermostat

Resolution

SER7300

In some application, the device may control baseboard heat or different controls and the user may want to stop the fan in heating mode.

The user shall set the Pulsed HT parameter to ON and Fan Cont to Off Auto and this will solve the issue.

 

SER8300

The user shall set Fan Cont to Off Auto and this will solve the issue.

 