How to extend the time period for Continuum Webclient user to log off automatically when there is no click on the web page

Issue

The default auto log off time setting is 20 minutes, customer need to extend the time period for web user.

Environment

  • Continuum Webclient
  • Windows XP
  • Windows Server 2003
  • Windows Server 2008

Cause

The default auto log off time setting is 20 minutes,  and can not modify the setting on cyberstation or webclient server

Resolution

  1. From the webclient install package, open "Webclient planning and installation guide.pdf",
  2. Reading from Page 105 to Page 106,
  3. Go to C:\Program Files\webserver, open web.config
  4. Go to "SessionState" tag and modify the value behind "timeout=" , the default is 20 in minutes. You can change it to another value if you prefer.
  5. Save and close web.config
  6. Log on web client to see the performance.