Issue

When a door is unlocked by schedule (or timed/permanent unlocked) the Continuum controller by design does not perform door ajar checking until the door re-locks.

At a site a Door is unlocked by schedule during business hours (8-5) but site still wants a door ajar alarm if someone goes thru the door and leaves it ajar.

Environment

CyberStation

CX9900

CX9702

CX9680

ACX5720

ACX5740

Cause

Documentation

Resolution

Write a PE program to monitor the door's DoorSwitch and set the DoorAjar flag as needed, care should be taken as to only engage the PE program when the access engine in the controller is shunting the alarm in order to avoid contention.

Click HERE to see a sample PE program

NOTE: Make sure to attach the DoorAjar alarm enrollment to the door.