Issue

How to relinquish a priority on multiple BACnet objects from a list view or search.

Environment

  • Workstation
  • Automation Server
  • Enterprise Server

Cause

Documentation

Resolution

1. In the list view or search select all of the objects in question (IMPORTANT: Only objects of the same class type should be selected)

2. Open the property grid by clicking the red checkmark.

3. Go to the Command tab and remove the value from the priority that is to be relinquished then save the change

NOTE:

As of 1.5 the above steps work ONLY for objects of analog type.

 

In the screen shot above, use back space to remove the 1 leaving the field blank and then save the change, SBO will relinquish priority 16 on all the objects selected in the liat view or search. 