How to run a controller program (InfinetProgram) when the controller first starts up?

Issue

How to run a controller program (InfinetProgram) when the controller first starts up?

Environment

Continuum Controllers Plain English

Cause

Need to be able to set specific parameters at startup time of the controller. For example, with a VAV controller, you may want to re-calibrate the closed position of a damper by having this done at power up. This will allow just a power cycle of the controller after been serviced locally.

Resolution

Have a program run at start-up of the controller that resets any required parameters back to default values.

To do this, create a Program that sets these values and then configure that Program with a FlowType of 'FallThru' and with AutoStart set to 'True'. This will run the program only once at start-up of the controller.
 