Issue

Sample PE program for setting attributes on all objects of a given class in a controller.

Environment

ALL CX Controllers.

Cause

The following PE program is a sample of a program that sets the site codes on ALL the doors found in the controller upon the controller power up.

Resolution

'This program sets the site codes on all the doors in this controller
'Program is autostart and fallthru
'Program is triggered by the MINUTE system variable
'12/16/2011 Abe Meran
'Sample program

Datetime LastStartUp
Object theDoor

INIT:
  LastStartUp = PowerUpTime
  Goto WAIT1

WAIT1:
  If PowerUpTime > LastStartUp then Goto RESET_SITE_CODE

RESET_SITE_CODE:
  OpenList("Door", theDoor)
  While GetObject(theDoor) is Success
    If theDoor Site1 = 0 then theDoor Site1 = 1
    If theDoor Site2 = 0 then theDoor Site2 = 2
    If theDoor Site3 = 0 then theDoor Site3 = 3
    If theDoor Site4 = 0 then theDoor Site4 = 4
  Endwhile
  CloseList(theDoor)
  Goto WAIT1

E:
  CloseList(theDoor)
  Goto WAIT1


Here is another example of a program residing in a CX that sets the site codes on all the doors of all the ACXs under the CX

Object theACX
Object theDoor
Number OK

If OpenList("InfinetCtlr", theACX) is Success then
  While GetObject(theACX) is Success
    If OpenList("Door", theDoor, theACX) is Success then
      While GetObject(theDoor) is Success
        theDoor Site1 = 1111
        theDoor Site2 = 2222
        theDoor Site3 = 3333
        theDoor Site4 = 4444
      Endwhile
    CloseList(theDoor)
    Endif
  Endwhile
Endif
Goto 2

2:
  CloseList(theACX)
  CloseList(theDoor)
Stop