Issue

How to set momentary duration (pulse duration) on a 7780?

Environment

I/NET site

Cause

How to set momentary duration (pulse duration) on a 7780?

Resolution

Using a Hand Held Console:

  1. Press [Code], then type 07 and press [Enter] to set momentary duration.
  2. The current momentary duration in milliseconds displays. Enter the desired delay in milliseconds and press [Enter]. The range is 0-255 (0-2.55 seconds). For example, entering 100 from the HHC results in a one-second pulse to the relay to turn it On or Off.
  3. When using a standard 7780, the momentary duration value should be set to a minimum value of 10 (0.1 seconds).