How to temporarily stop a schedule from driving its occupancy point.

Issue

For various reasons it may be necessary to temporarily stop a schedule from driving its occupancy point, is there an easy way to accomplish this?

Environment

CyberStation

All CXs

All i2s

All b3s

Cause

Documentation

Resolution

If the schedule object is a Continuum schedule...

1. Edit the schedule object

2. Go to the 'Configuration' tab

3. Set the state to disabled.

For a BACnet schedule...

1. Edit the schedule object.

2. Go to the 'Current State' tab

3 Check the 'Out of service' box

 To return control to the schedule re-enable it/put it back in service.