I/A Series G3 ENC cannot communicate with an MZII controller after the MZII controller has been power cycled.

Issue

After powering down a Microzone II controller and powering it back up, the ENC will not immediately reconnect to the device.

Environment

I/A Series G3 ENC with tacASD 3.4.64.1 or earlier module (jar file).

Any ASD devices under the ENC.

Cause

The existing tacAsd module, (release 3.4.64.1 or earlier) may exhibit excessive device initialization and recovery times upon a restart of the station or a power cycle of the ASD devices.

Resolution

Update the tacAsd module to release 3.4.64.4.

File acAsd-3.4.64.4 can be downloaded from Ecobuildings Download Center.