I/A Series ProView LON display SCHEDULE ERROR: Special day 1 event 2 time must be greater than event 1 time.

Issue

I/A Series ProView LON display SCHEDULE ERROR: Special day 1 event 2 time must be greater than event 1 time.

Environment

I/A Series ProView LON Display

Cause

Typically caused by attempting to use a previously commissioned and active copy the I/A Series R2 lonProview jar file ECDIS210 shadow object.

Resolution

Power cycle the display.

Use the ProView wizard and on the first screen, select Schedule from the Page Selection drop down list.  The Calendar screen should display, select next to move to the Week Schedules.  Select next to display the Special Days screen.  Review the event times entered for Special Day 1 (especially Event 1 and Event 2).  Make sure the times that are entered are in ascending order from midnight (00:00).

Review Holiday1 to Holiday 4 and modify the enumeration on all events to "no event."

Commit the changes to the display.