I/NET Controller in StruxureWare Building Operation has a blue circle with a white down arrow on top of it.

Issue

I/NET Controller in StruxureWare Building Operation has a blue circle with a white down arrow on top of it.

Environment

I/NET Integration

StruxureWare Building Operation

Cause

Any change to the I/NET controller will result in this indication requesting an upload. Changing a configuration in a time schedule or updating a calc extension on a point are two examples of what might cause this.

Please note that the Upload DOES NOT complete the same action as a Station Save in I/NET. Upload will sync the StruxureWare Database with the I/NET database. To perform a station save from StruxureWare, right click on the Controller and select "backup".

Resolution

  1. Expand the I/NET Interface network object
  2. Right click on the offending controller
  3. Select Upload
  4. Wait a few seconds. A refresh of the System Tree may be required.