I/NET Values not updating in StruxureWare Building Operation Workstation

Issue

Values only appear to update in Workstation when performing an upload.

Environment

I/NET Seven 2.43 and above

StruxureWare Building Operation 1.3.0.978 and above

Cause

I/NET Interface Global scan rates are set to 0 (disabled)

Resolution

The Global scan rates defined within the properties of the I/NET Interface should be set to a value greater than 0 to display and automatically update values and controller status from the I/NET system.  The default settings are set to 60 seconds and 5 seconds for the device updates and point updates respectively.

Image below shows the location of these settings within Workstation: