If you have a double address on an SCU 1284, and the operation of the LEDs are wrong after you installed I/NET Seven rev 2.21 what do you do?

Issue

If you have a double address on an SCU 1284, and the operation of the LEDs are wrong after you installed I/NET Seven rev 2.21 what do you do?

Environment

I/NET Seven rev 2.21

SCU 1284

Cause

I/NET Site

Resolution

If you had set a double address in the SCU 1284, the operation of the LEDs are wrong. Both LED (Green and Red) are active permanently no matter what you set in the Door Editor(Anode/Cathode), the LED will just flash once when the door is operated. If the SCU is set to single address, the LED will work correctly. The equipment setting that will cause this issue is having a 7798C with BIN file Rev 1.08 and SCU1284 with BIN Rev 3.25. To correct this issue requires you to only change the BIN file in the 7798C from rev 1.08 back to Rev 1.06. This 1.06 Bin file is from the I/NET Seven rev 2.16 release. Please note the SCU1284 LED issue DOES NOT exist in the following BIN files in the I/NET Seven rev 2.21 release. 7798B Bin is OK 7793 Bin is OK SCU1284 Bin(3.25) is OK