Importing a Xenta 121-FC controller into StruxureWare Building Operation.

Issue

Importing a Xenta 121-FC controller into StruxureWare Building Operation.

Environment

Xenta 121FC

Cause

How do you setup the Xenta 121-FC using StruxureWare Building Operation only, as all the config needs setting for 1 Return Temp. Cooling Only (AO type). Fan On/Off
 

Resolution

The original process would require the use of LonMaker and ZBuilder to configure the Xenta 121-FC controller onto the LON network, before adding it to the StruxureWare Building Operation LON interface.

Version 1.4 introduces LNS device plug-in support to configure LonWorks® devices. StruxureWare Building Operation v1.4 supports third party software: OpenLNS. OpenLNS is only required on WorkStation machines used for configuration of LON® devices (e.g. WorkStation Pro machines). Automation Server and Enterprise Server databases are updated with any changes created with the plug-in.

With LNS device plug-in support, now ZBuilder can be used with SmartStruxure solution. Plus, all Xenta controllers are supported, including the X100 series – e.g. Xenta 121.