In Niagara R2, master-slave schedules are not working. The slave schedule goes into fault and will not clear. The following error appears in the standard output window of the UNC...

Issue

In Niagara R2, master-slave schedules are not working. The slave schedule goes into fault and will not clear.  The following error appears in the standard output window of the UNC:
 

ERROR: Could not init node [/OZS_UNC1/IbsAsdNetwork/AHU_9/MZ2_93/Schedule_8]

Environment

Niagara R2

Cause

This error, and subsequent fault condition on the schedule object, can occur when the Enterprise Server has a holiday calendar and a master schedule and the UNC only has a slave schedule.

When the UNC is rebooted (for other reasons), the slave schedule object checks the master schedule object in the server to see if it's a holiday.  If there is a communication issue, the slave schedule object goes into fault.

Resolution

Delete and re-create the slave schedule object.

Add a master/slave schedule AND master/slave calendar objects in the server and UNC stations.