Issue

 

In Niagara R2, what would cause an IP communication to the UNC to drop out?  There are no errors in the standard output window.

Environment

Niagara R2 All version; UNC-410, UNC-510, UNC-520

Cause

The same IP address is assign to more than on controller. Two UNC controllers are using the same IP address.

Resolution

This symptom usually indicates a duplicate IP address condition. Under this condition the UNC will keep dropping offline for a period of time.  The duplicate IP address situation will need to be corrected before reliable communications can be established.

Reassign one of the UNCs a different IP address that is not currently being used.  Ensure that each IP address is only assigned to one controller.