Issue

In OPRIF 11.6, the "database save" command does not work.  When pressing "S" for save, the first prompt asks for the drive letter where the files will be saved (i.e. C drive).  After pressing enter, the second prompt requests a filename.  An eight-digit filename can be entered.  A file path is optional.  After pressing enter, a new screen should appear as the database save begins. 

However, after pressing enter, the screen returns to the main database menu.

There are no errors reported.

Environment

DMS

OPRIF 11.x

Cause

A graphic screen is missing from the installation of OPRIF.  After entering the driver letter and filename for the database save, a new screen should appear.  The graphic file is requested but doesn't exist.  As a result, the database save command aborts and returns to the main database menu screen.

Resolution

The simplest solution is to re-install OPRIF 11.6 "overtop" the existing installation.  The missing file(s) will install.