In a G3 Enterprise Server, " ERROR [08:29:26 31-May-13 CDT][web.server] HTTP Server failed to bind to port. Address already in use: JVM_Bind"

Issue

MESSAGE [08:29:10 31-May-13 CDT][sys] *** Station Started (203ms) [1919ms total] ***
niagara>MESSAGE [08:29:12 31-May-13 CDT][history.db] Starting async warmup of history config index...
MESSAGE [08:29:12 31-May-13 CDT][history.db] Async history config index warmup completed in 15 ms.
ERROR [08:29:16 31-May-13 CDT][web.server] HTTP Server failed to bind to port. Address already in use: JVM_Bind
ERROR [08:29:21 31-May-13 CDT][web.server] HTTP Server failed to bind to port. Address already in use: JVM_Bind

Environment

I/A Series G3 Enterprise Server, all versions

Cause

Another service on the pc is using port 80, conflicting with the Enterprise Server.

For example,  Skype  will use port 80 as an alternative unless you uncheck the box in Skype options.

As a second example, another Niagara station may be running on the same computer.

See article #6203 for a similar port  conflict issue with SmartStruxure.

Resolution

In the Skype menu; Tools  /Options / Advanced / Connection, uncheck the box for "Use port 80 and 443 as alternatives for incoming connections"