Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Infinity Schedule objects can only be configured to control local InfinityNumerics or InfinityOutputs.

Issue

When configuring an Infinity Schedule, why can't I select an object from another controller for the Occupancy Point?

Environment

  • Continuum
  • CyberStation
  • WebClient
  • Schedules
  • InfinityController

Cause

Trying to configure a schedule to control a remote point.

Resolution

  • Infinity Schedule objects must control points that reside in the controller in which the schedule resides.
  • Continuum will not allow you to browse to or select points that reside in controllers other than the controller that the schedule resides in.